I am currently using Modbus TCP on an A12 running Qlarity. Normally I am communicating with 3 to 4 slaves. Communication runs fine and updates values for about a week and then quits communicating. After a screen reboot the communication is restored. Any thoughts about why this may be?


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 9:59 am 
Offline
User avatar

Joined: Thu Mar 02, 2006 2:12 pm
Posts: 487
Location: Salt Lake City, Utah
This is not something I've experienced or had reported on the QTERM-A12 before.

Can you describe the behavior you are seeing when communication stops. Are you getting error messages? Is the display locked up? Are you able to ping the QTERM-A12? Are you able to ping all of the other Modbus devices?

It would also be helpful to see a packet sniff of the communication when this happens from a program such as "WireShark".
http://www.wireshark.org/

_________________
Ron L.

http://www.beijerelectronicsinc.com/


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 10:41 am 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
I have not tried to ping the terminal yet, we had a client come across this problem and are trying to reproduce the issue now. The screen is not giving any error messages and is not locked up, it just appears as if it is not reading the new values. All buttons and commands that are internal to the screen are still operational.

If we reproduce the issue with our bench test I will ping and packet sniff the terminal.


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 1:08 pm 
Offline
User avatar

Joined: Thu Mar 02, 2006 2:12 pm
Posts: 487
Location: Salt Lake City, Utah
It sounds like you have changed the "messagefilter" property of the ModbusComm to hide error messages. I would recommend turning that on to see what communication errors are occuring.

_________________
Ron L.

http://www.beijerelectronicsinc.com/


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 1:45 pm 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
Thanks for the reply. I turned the error messages back on and get the following error on all slave devices:

Parsing error, or possible out of sync. packet, resetting modbus comm.


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 1:51 pm 
Offline
User avatar

Joined: Thu Mar 02, 2006 2:12 pm
Posts: 487
Location: Salt Lake City, Utah
That's a strange error message to get. I would not expect that unless the device you're talking to is not adhering to Modbus protocol. I'd be curious to see what the communication looks like between the two devices from a packet sniff program such as "WireShark". Are you using the ModbusV2 library included with Qlarity Foundry 2.63?

_________________
Ron L.

http://www.beijerelectronicsinc.com/


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 2:53 pm 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
I am using the modbusV2 library included with Qlarity Foundry 2.63. I am also able to receive and send data on the modbus network despite the error messages posted earlier. I have some data collected from the wireshark program. I am unable to attach the pcap extension on the forum however. Please advise.


Top
 Profile  
 
PostPosted: Mon Oct 17, 2011 3:10 pm 
Offline
QSI Support
QSI Support
User avatar

Joined: Wed Mar 08, 2006 12:25 pm
Posts: 881
Location: Salt Lake City, Utah
Try zipping it up. The forum software only allows certain extension, but .zip should be fine

_________________
Jeremy
http://www.beijerinc.com


Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 6:26 am 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
Ron,

My e-mail was sent back. Here is what we have so far:

These two files are from the wireshark program. One prior to the comms failure on our bench test and one after the failure which occurred sometime last night. The file labeled ashdown comms fail is after the failure. Two of the devices we have are showing up on the A12 (111.111.111.106 and 111.111.111.107) The third device (111.111.111.109) is the one that is no longer communicating. Is there any other info you need? Thanks in advance for your help in this matter.


Attachments:
ashdown_comms_fail_10_18_11.zip [2.33 KiB]
Downloaded 173 times
test_ashdown_1.zip [36.05 KiB]
Downloaded 184 times


Last edited by Dano.oh on Tue Oct 18, 2011 8:00 am, edited 1 time in total.
Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 7:52 am 
Offline
User avatar

Joined: Thu Mar 02, 2006 2:12 pm
Posts: 487
Location: Salt Lake City, Utah
I do show IP address 111.111.111.109 reseting its TCP/IP connection for no apparent reason.

Were you seeing an error message displayed during this sniff? If so, what was the exact text?

Everything else looks normal. Can you narrow this down to a Single Modbus Comm object and Single MRegister object. The error message that appears might indicate which objects query failed.

_________________
Ron L.

http://www.beijerelectronicsinc.com/


Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 8:12 am 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
The errors we are getting (during the sniff also) are:

"modbuscomm983en1: Parsing error, or possible out of sync. packet, resetting modbus comm."
"modbuscomm983en2: Parsing error, or possible out of sync. packet, resetting modbus comm."

We had a similar error message before the comms failure which was:

"modbuscommDECS1: Parsing error, or possible out of sync. packet, resetting modbus comm."

Now we are still getting the first two error messages, but the third device 'modbuscommDECS1' won't send or receive.

The first two devices are send only.


Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 8:18 am 
Offline
User avatar

Joined: Thu Mar 02, 2006 2:12 pm
Posts: 487
Location: Salt Lake City, Utah
Can you create a workspace with two objects that causes the error message: 1 ModbusComm and 1 MBRegisterV2? Then send me a packet sniff of this communication and a copy of the simplified workspace?

_________________
Ron L.

http://www.beijerelectronicsinc.com/


Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 9:56 am 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
Unfortunately we aren't able to duplicate the failure with a simplified workspace. The simplified workspace has no errors. Do the error messages we are getting help us narrow the search for where this error is occurring?


Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 10:09 am 
Offline
User avatar

Joined: Thu Mar 02, 2006 2:12 pm
Posts: 487
Location: Salt Lake City, Utah
Are the objects: modbuscomm983en1, modbuscomm983en2, modbuscommDECS1 ModbusComm objects? What are there IP Address of them?

If the "wordsize" set to mb_16bit? (this is what 99% of the Modbus devices use).

_________________
Ron L.

http://www.beijerelectronicsinc.com/


Top
 Profile  
 
PostPosted: Tue Oct 18, 2011 10:31 am 
Offline
User avatar

Joined: Wed Feb 02, 2011 9:20 am
Posts: 20
Yes those are modbuscomm objects. The IP of each respectively are: 111.111.111.107, 111.111.111.106, and 111.111.111.109. The wordsize is set to mb_16bit.


Top
 Profile  
 
Display posts from previous:  Sort by  
Post new topic Reply to topic  [ 16 posts ]  Go to page 1, 2  Next

All times are UTC - 7 hours


You cannot post new topics in this forum
You cannot reply to topics in this forum
You cannot edit your posts in this forum
You cannot delete your posts in this forum
You cannot post attachments in this forum

Search for:
Jump to:  
cron
Powered by phpBB® Forum Software © phpBB Group